That would be 10ga so sayeth the Baldor spec sheet...........................
https://www.baldor.com/catalog/L1430T
Thanks, Hinder.
View attachment 41742
Also remember that 10g stranded wire is about 10% larger than 10g solid wire.
Thanks again, Skipper.
I find it interesting that the 3 charts I listed give different information.
We'll see what happens.
I have 8ga wire from the 40A breaker on the main panel to the sub panel.
I don't wanna have to redo that with heavier wire.
I guess if I need a bigger breaker the 8ga will handle a inrush 60A load.....(?)
Mebbe I'll git 'er cone today and see what happens.
Problem I'm limping into now is that the starter is rated for 5hp, but it dunna wanna accept 8ga wire............
People are tellin' me to use 10ga..................
Ron,
That you were provided with three different methods from three different charts is mostly due to the fact that you didn't review five or six different charts, then you would have had five or six different opinions to chose from.
Not to worry amigo, I suspect it will work just fine.
Rog
The motor only draws 22A or so when running, and start up when it pulls the most, is quick.
The "lugs" or, should I say...screw terminals just would NOT handle 8ga.
Period.
I contacted the seller of the starter and he said"we sell 50 gazillion if these every minute to compressor companies and they ALL use 10ga."
He also added "we have 3 compressor engineers on staff and they ALL say '10ga' "
Bla bla bla bla..."If you want to use 8ga install lugs."
So, I used 40A breaker and 10ga wire (6' from breaker to starter, and 2 feet from starter to motor) and...................
Wait for it...........
Wait for it...........
Wait for it...........
Wait for it...........
IT WORKS !! Wires do not get hot; compressor pumped up to 150 without a problem.
I'll bump up the pressure to test tomorrow.
There is a situation of 2 wires of dissimilar gage having to fit the same terminal..........pain in the buttocks.....
cuz the small wire dunna wanna get tight....so I have to insert a stub of another wire to make the little one "bigger."
Look on the MOTOR DATA PLATE .. what is the FLA numbers & if shown LRA numbers You may want to change the breaker to a 30AMP if you're using #10 THHN jacketed wire (just precautionary)
Dickhead??? I believe that is Mister Dickhead to you my friend. Life is getting in the way and a possible health issue. Will know more after I see a specialist on tbe 12th
Tom
Look on the MOTOR DATA PLATE .. what is the FLA numbers & if shown LRA numbers You may want to change the breaker to a 30AMP if you're using #10 THHN jacketed wire (just precautionary)
You may de-rate the wire by using #10 pigtails and wire nutting the #8 to it. Or use Burndy split bolt connectors, or some other means of connecting the two together.. Maybe just snip a couple strands out of the #8 unless it's solid wire.
Ron,
HOORAY!!! I knew it would work. Hey, just for fun, if you have a spare 30-Amp two pole breaker laying around, try swapping it for the 40-amp and see if it will stand the start-up current. At least that way the circuit won't be over protected. 30 amps is safe for up to 24 amps (running) and #10 wire is rated for 30-A. Then if the garage burns down, the insurance inspector won't be able to deny your claim because it wasn't wired correctly.. (Believe me it happens!!)
You done good!!
Rog