PTmowerMech
- Apr 16, 2018
- 432
- 3,315
There are different ways to manufacturers wire up portable generators. If engine is running at approx 3600 and you have 183v at the outlet most likely the AVR is bad. Have you checked the 240v outlet voltage? Across the 2 hots, each hot to the neutral.
Most portable generators with 240v will have 2 separate 120v outlets with each one using a hot leg of the 240 to neutral so you can utilize all the generator's power into 2 120v circuits. Looks like that one only has one duplex receptacle so they are either just using one leg of the 240 or they have split the outlet with a different leg to each socket. You can test it by measuring between the two hots of the receptacle. Zero volts on one leg. 240v means the receptacle is split using both 240v legs.
Checked the 220v legs and got the same 180V.